Does the monitoring portal show when modules are shut down?

Kommentare

6 Kommentare

  • Avatar
    Dean Ting

    When rapid shutdown is triggered, all the panels on monitoring portal will report zero power production and an alert will be generated, this could be used to tell whether rapid shutdown is enabled or not. 

    1
  • Avatar
    Jesse Campbell

    Thanks!

    0
  • Avatar
    Adolf Schnecker

    Alert is generated immediately or is it delayed?

    0
  • Avatar
    Gary Hethcoat

    Hi Adolf, alerts like this may not come immediately.  There may be a delay of 15 minutes to a few hours depending on what is happening on the system.

    0
  • Avatar
    Jesse Campbell

    I have tested with my system. The portal does report 0 watts for all units, and I got a text message alert within a minute or two of activation. As Gary says, that's not guaranteed though.

    0
  • Avatar
    Gary Hethcoat

    One other thing -- events lasting less than 10-15 minutes may not trigger an alert.  This is something to keep in mind, particularly if you want to test the system.  It is best to perform rapid shutdown and leave the system off for 30 minutes to be sure the alert is generated.

    0